Brewing Discussions => Equipment & Chemicals => Topic started by: mcgrath on February 20, 2014, 08:21:40 PM

Title: stc 1000 problem
Post by: mcgrath on February 20, 2014, 08:21:40 PM
Wired up one today to control fermentation fridge. When the cool indicator comes on its not sending power to fridge. Anyone ever had this problem?  There's a 10amp fuse inside. I'll prob open it up and check it out but not sure how simple that will be. I've wired one before and had no problems.
Cheers...
Title: Re: stc 1000 problem
Post by: johnrm on February 20, 2014, 09:41:17 PM
Do to hear a click from the stc when cooling kicks in?
Have you a multimeter? Check for circuit open/closed across cooling with no load connected.
There could be a long delay set on cooling.
Title: Re: stc 1000 problem
Post by: mcgrath on February 21, 2014, 12:49:18 AM
Yeah its flashing not constant. I'll check again when I'm there tomorrow. Maybe patience is all that's required :-) fingers crossed.
Title: Re: stc 1000 problem
Post by: mcgrath on February 22, 2014, 08:31:04 PM
Cheers lads you were spot on. Mine came programmed with 3 minute delay. I didn't give it enough time. Happily fermenting at steady temp now ;-)
Title: Re: stc 1000 problem
Post by: Ciderhead on February 22, 2014, 08:44:18 PM
1 degree differential and 10 min delay works best for stc's